kingtutley
Electrical
- May 11, 2007
- 49
I am a relatively recent grad and am still trying to learn what I assume are basics of the power protection systems in fossil power plants.
I am working to gain an understanding of the operation of LV and MV switchgear/breakers etc. I have manual from Schneider that I downloaded from their web site, but I just don't get it.
Attached is a page that shows what they say represents the typical control circuit scheme. This makes no sense to me. If I read this right, then the breaker won't stay closed.
Looking only at the Trip Circuit in the middle, the 2 52a contacts should close when the breaker is closed, right? Well, this charges the 52/TC (Trip Coil). Won't this trip the breaker? What did I miss?
Aside from this, according to the manual, the 52Y coil (Anti-Pump Relay) is supposed to keep the breaker from pumping open and closed if there should be a trip signal when the close circuit is energized. What? Again, if I read this right, the close coil will be energized, and close the breaker, only if it is open (52b contact in series), and the springs must be charged (52LS) and latched -- which means that it is ready to operate (52LC). But if the breaker has ever been closed, then the 52Y coil will ALWAYS bee charged (aside from loss of control power) and hence wil ALWAYS prevent the closing coil from being energized. What am I missing? Am I just that far off?
I am working to gain an understanding of the operation of LV and MV switchgear/breakers etc. I have manual from Schneider that I downloaded from their web site, but I just don't get it.
Attached is a page that shows what they say represents the typical control circuit scheme. This makes no sense to me. If I read this right, then the breaker won't stay closed.
Looking only at the Trip Circuit in the middle, the 2 52a contacts should close when the breaker is closed, right? Well, this charges the 52/TC (Trip Coil). Won't this trip the breaker? What did I miss?
Aside from this, according to the manual, the 52Y coil (Anti-Pump Relay) is supposed to keep the breaker from pumping open and closed if there should be a trip signal when the close circuit is energized. What? Again, if I read this right, the close coil will be energized, and close the breaker, only if it is open (52b contact in series), and the springs must be charged (52LS) and latched -- which means that it is ready to operate (52LC). But if the breaker has ever been closed, then the 52Y coil will ALWAYS bee charged (aside from loss of control power) and hence wil ALWAYS prevent the closing coil from being energized. What am I missing? Am I just that far off?