I need to supply 800 GPM (540 GPM to sprinklers and 250 GPM hose allowance)to a combination fire protection system. Can 4" line be used between street main and a riser? System's riser was sized to be 4". NFPA 13, section 8-2.1 requires a flow rate no less than 390 GPM thru 4" line to obtain at least 10 ft/s velocity, but it does not set an upper limit. Does anyone know what it is?
I know that this rate of flow thru 4" pipe will generate 20.2 ft./s velocity and pressure loss of 0.18 psi/100 ft. of pipe. I wonder if 4" line can be used with these flow parameters, assuming of course, that it will deliver required GPM at required min. pressure. Thx!
I know that this rate of flow thru 4" pipe will generate 20.2 ft./s velocity and pressure loss of 0.18 psi/100 ft. of pipe. I wonder if 4" line can be used with these flow parameters, assuming of course, that it will deliver required GPM at required min. pressure. Thx!