DCBII
Structural
- Apr 15, 2010
- 187
I'm anchoring a masonry wall to a flexible diaphragm. I've calculated the anchorage force per ASCE 7-10 Section 12.11.2.1 as 0.4SDSIekaWp = 5.4 kip. If these were concrete anchors, ACI would require either: (1) a ductile failure mechanism, or (2) design for the amplified seismic load (a.k.a. overstrength). The masonry code does not hold me to any such requirements with regard to anchor design. The IBC does not either. Should this connection be designed for overstrength?