Managing Spares PSV 1

Status
Not open for further replies.

Corgas

Materials
Dec 22, 2008
115
Steam valve on Waste Heat Boiler (475 psig set pressure).

Valve was tested in 2013 and sat on shelf for 3 years and it was put in service in 2016.

Operator says it's not past due since it's been in service for only two years even though last test date was in 2013.

Is it past due? has anyone come cross this situation?
 
Replies continue below

Recommended for you

I would think it has to be re-tested. How can you verify/certify that the valve wasn't used during that period? Or that the valve wasn't modified in that time.
 
RVAmeche is correct with that statement. However, It is recommended that testing is done immediately prior to installation to ensure that the valve is set correctly. These are delicate instruments and carraige, handling etc., can and has an affect on the setting.

NB: Being a Safety Valve on steam, it should be fitted with a lever. This is an ASME mandated requirement to check the valve periodically that it works - NOT a set pressure setting test, but to check its functionability. This is from the old days when untreated water tended to stick the valve internals. Unfortunately the lever is wrongly sometimes used for physically lifting the valve during the manhandling causing damage to seats and spindle.

Best test to do now is on the boiler itself, but this requires specialist operators, and what if the valve does not work? In-situ testing using outside equipment can check set pressure but not seat condition, full opening/closing, condition of internals etc.

There is also local authority, insurer and valve suppliers requirements to note.

The SV is there to protect life and property as a last resort. Don't compromise this safety

Per ISO, only the term Safety Valve is used regardless of application or design.
 
Thanks RVAmeche and avalveman.
 