- Nov 7, 2008
- 28
We have a generator that needs to be load bank tested. The output is 480V 3P 1000A. The test will be limited to 800A and we are installing a separate 1000A circuit breaker in an I-line panel to go to the load bank.
The methods I have seen so far for hooking up a rented load bank is to connect 4/0 welding cable into a circuit breaker with the panel exposed for the duration of the test. It works but violates a number of safety regulations. I want to use a panel of Cam-lok lugs (E1017 series) and have the contractor plug his 2 sets of 4/0 cables. According to to what I find in the NEC I need 700MCM cables for use in a raceway/conduit. My problem is I don't have room left in the panel for 700MCM cables. Is there a legal justification for using 4/0 cable for a short run, <6 feet, to the cam-lok lugs or perhaps a better method?
The methods I have seen so far for hooking up a rented load bank is to connect 4/0 welding cable into a circuit breaker with the panel exposed for the duration of the test. It works but violates a number of safety regulations. I want to use a panel of Cam-lok lugs (E1017 series) and have the contractor plug his 2 sets of 4/0 cables. According to to what I find in the NEC I need 700MCM cables for use in a raceway/conduit. My problem is I don't have room left in the panel for 700MCM cables. Is there a legal justification for using 4/0 cable for a short run, <6 feet, to the cam-lok lugs or perhaps a better method?