I have an existing shell and tube HX with the following design values:
190 GPM both sides
Hot inlet 220ºF
Hot out 200ºF
Cold in 165ºF
Hot out 185ºF
I want my cold in and out to be 140 and 160ºF
This increases my LMTD from 31 to 48 (includes correction factor for hybrid design). At the design value I needed 1.8MMBTU/hr, and now I see that I need 2.7MMBTU. Will this work, or does the increased LMTD affect my "U" value, negating the extra BTU/hr that I add on the hot side?
Thanks