jharris3
Mechanical
- May 3, 2011
- 52
I am an ME commissioning a small oilfield produced water filtration plant and we have some problems with gas developing in the suction lines to the pumps. I would like to know what sorts of chemical additives could be used to help the gases separate out of the produced water upstream in the associated Oil Cleaning Plant (OCP) if any.
The OCP is a "light oil" plant that has some deep wells where fuel gas injected for gas-lift. Operations claims to remove the gas at the gage setting before the OCP. The OCP is a Wash-Skim-LACT tank configuration, however, the Skim tank is out of service for nearly two years. We have already made plans to clean the skim tank ASAP and put the plant back into a more normal configuration or at least into a more clean tank. We have in the meantime installed a connection to the wash tank that is on the outlet side of the tank.
The holdup time for the PW in the Wash tank is between 5 and 7 hours normally, but due to the solids buildup in the tank the holdup time is down to 4-6 hours (based on interface). When the water reaches the injection plant (WIP) there are two surge tanks that are connected together and operate with approximately 4-6 hours more hold up time combined. After the filters (walnut shell - adsorbers) there is an equally sized tank for the injection water that operates at a higher level so that the hold-up time would normally be 5-8 hours.
With all that hold up time gas is breaking out in the suction piping to all the pumps. The injection pumps aren't even running but a pretty good amount of gas breaks out, and no I haven't been able to obtain a consistent result of how much gas breaks out for a given volume of liquid. All I can say is that the suction lines are not sloped back to the tanks sufficiently and about 1"-2" of space in the top of the pipe fills with gas, but for what length of pipe I don't know. After I bleed the line I can come back in a few hours and bleed nearly the same amount of gas off again. This can continue for over a week.
I have had some testing done to tell us what is in the PW which by the numbers appears to be C10-C36 in various ppm quantities mostly C10-C20. The gas breaking out is 85% methane (mol), 2.42% ethane, 1.195% propane, 1.653 % hexane, and 6.154 % CO2.
Can an additive be used to help the gas break out faster so that it does so in the tanks rather than the pipe? Can ana additive be used to keep the gas from breaking out at all? This is preventing performance in the pumps.
The pumps we realize are high energy pumps (Nss = 12000) and require a 1.7 Margin on NPSHr and that is likely part of our problem. We might persue some other options with the pumps but for now I would like to know what can be done on the process side.
The OCP is a "light oil" plant that has some deep wells where fuel gas injected for gas-lift. Operations claims to remove the gas at the gage setting before the OCP. The OCP is a Wash-Skim-LACT tank configuration, however, the Skim tank is out of service for nearly two years. We have already made plans to clean the skim tank ASAP and put the plant back into a more normal configuration or at least into a more clean tank. We have in the meantime installed a connection to the wash tank that is on the outlet side of the tank.
The holdup time for the PW in the Wash tank is between 5 and 7 hours normally, but due to the solids buildup in the tank the holdup time is down to 4-6 hours (based on interface). When the water reaches the injection plant (WIP) there are two surge tanks that are connected together and operate with approximately 4-6 hours more hold up time combined. After the filters (walnut shell - adsorbers) there is an equally sized tank for the injection water that operates at a higher level so that the hold-up time would normally be 5-8 hours.
With all that hold up time gas is breaking out in the suction piping to all the pumps. The injection pumps aren't even running but a pretty good amount of gas breaks out, and no I haven't been able to obtain a consistent result of how much gas breaks out for a given volume of liquid. All I can say is that the suction lines are not sloped back to the tanks sufficiently and about 1"-2" of space in the top of the pipe fills with gas, but for what length of pipe I don't know. After I bleed the line I can come back in a few hours and bleed nearly the same amount of gas off again. This can continue for over a week.
I have had some testing done to tell us what is in the PW which by the numbers appears to be C10-C36 in various ppm quantities mostly C10-C20. The gas breaking out is 85% methane (mol), 2.42% ethane, 1.195% propane, 1.653 % hexane, and 6.154 % CO2.
Can an additive be used to help the gas break out faster so that it does so in the tanks rather than the pipe? Can ana additive be used to keep the gas from breaking out at all? This is preventing performance in the pumps.
The pumps we realize are high energy pumps (Nss = 12000) and require a 1.7 Margin on NPSHr and that is likely part of our problem. We might persue some other options with the pumps but for now I would like to know what can be done on the process side.