I'm designing a maintenance platform - interior, no wind, seismic is negligible. I know there have been a few threads on this, but none seem to reach a rational conclusion and none seem to bring up an idea that I have, so I want to float it to see what others think.
Assume a 300# pedestrian (big guy carrying a big case of tools). If he's walking at 3.1mph (Wikipedia's average walking speed), or 4.55fps, is taking one step per second, and stops in one step, the force to stop him his:
F=ma
F=(300#/32.2ft/s2)*(4.55ft/s^2) = 42.4#, or about 14% of the applied gravity load.
This agrees pretty closely with the results found here, so I'm confident in the validity of my idea.
Now the question is how to apply it. In the linked article, they're looking at decks/balconies where a group of party-goers may do some sort of big, coordinated dance. This is an industrial application. No dancing, no synchronized marching, etc. Anyone have a suggestion for developing a rational application of this lateral load? If I design the platform for 100psf to account for personnel and material, a 14psf traction load on the whole surface feels like a bit much. Maybe a 60*0.14=8.4psf traction load based on a 60psf personnel loading for maintenance platform?
What do you guys think?
Assume a 300# pedestrian (big guy carrying a big case of tools). If he's walking at 3.1mph (Wikipedia's average walking speed), or 4.55fps, is taking one step per second, and stops in one step, the force to stop him his:
F=ma
F=(300#/32.2ft/s2)*(4.55ft/s^2) = 42.4#, or about 14% of the applied gravity load.
This agrees pretty closely with the results found here, so I'm confident in the validity of my idea.
Now the question is how to apply it. In the linked article, they're looking at decks/balconies where a group of party-goers may do some sort of big, coordinated dance. This is an industrial application. No dancing, no synchronized marching, etc. Anyone have a suggestion for developing a rational application of this lateral load? If I design the platform for 100psf to account for personnel and material, a 14psf traction load on the whole surface feels like a bit much. Maybe a 60*0.14=8.4psf traction load based on a 60psf personnel loading for maintenance platform?
What do you guys think?