Please see attached scan:
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1437659196/tips/Scan_xnx3b2.pdf[/url]

A quick summary:

Existing Design - MV Starter feeds a 500hp motor via undeground conduit.
Proposed Design - Use the MV starter to feed a MV VFD, and then re-use the underground conduit to feed the motor.

I'm curious to know if it is acceptable to route the cable between the VFD and motor via the MV starter section. We've made sure that there is sufficient space, cutout sections at the top, and no interferences.

The cable would be routed through the starter section inside a conduit, as shown in the attached photo.

ER5_-_Exhaust_Fan_Routing_2_pvdbn4.jpg
 
Replies continue below

Recommended for you

Where is the lockout for this motor, it is not shown in the your drawing. Also why have starter and a VFD in series? Remove the starter from system and go only with the VFD.
good luck,
Dave
 
The lockout will be on the VFD.

I don't have another supply available hence using the starter and vfd in series.
 
I don't understrand... are you WIRING the starter in series with the VFD? Most MV VFDs need to have a controller / controlled breaker ahead of them anyway, so I don't see the problem. Nut if you are using the starter ENCLOSURE just as a raceway for the FEEDER circuit to the VFD, that might be a problem.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 
I am reasonably sure you could run the motor cable through the starter, but am not sure that you can run the conduit though the stater.
However I can't think of a code rule that says you can't run the conduit through the starter.
 