HenryOhm
- Jun 22, 2005
- 60
I am working with an energy storage application. A three-winding transformer is in use. The utility feeds the primary winding medium voltage. One low-voltage secondary feeds an energy storage inverter with lithium-ion behind it. The third winding steps down the utility power and feeds a lower level of medium-voltage to the AC loads. When not on utility, the inverter and batteries step up and feed the AC loads through the two "secondary" windings. When the utility comes back on line, there will be a transition period as the inverter goes from discharge mode back to charge mode. This transition will lead to the AC loads transitioning from battery to utility power.
However, at the point that the inverter synchronizes with utility and the utility breaker closes back in, will the utility see little or no inrush on the primary (energized) winding? I want to say that there will be no inrush but I just can't get my head around this completely. Thanks.