IBC 1607.12.1 Distribution of roof live loads (skip loading)

Status
Not open for further replies.

jeffhed

Structural
Mar 23, 2007
286
I have always been taught (and required for plan review) to use skip loading on roof members, especially cantilevers. But I have always wondered if it was really required as I can't find anywhere in the code(s) that specifically state that pattern loading is required on roofs. All I can find where it actually says to use skip loading on roofs is IBC 1607.12.1. which reads as follows:

1607.12.1 Distribution of roof loads. Where uniform roof live loads are reduced to less than 20 psf (0.96 kN/m2)
in accordance with Section 1607.12.2.1 and are applied to the design of structural members arranged so as to create
continuity, the reduced roof live load shall be applied to adjacent spans or to alternate spans, whichever produces
the most unfavorable load effect. See Section 1607.12.2 for reductions in minimum roof live loads and Section 7.5
of ASCE 7 for partial snow loading.

When I read that section, it seems to imply that if I reduce the roof live load to less than 20 psf then I must consider skip loading and I should refer to ASCE 7 section 7.5 and apply the skip loading similar to how I would snow loads. It seems to me when I read it, that skip loading is ONLY required if you reduce live loads to less than 20 psf. If this was always required, then why would section 1607.12.1 talk about reduced roof live loads at all? Wouldn't that section just say the same thing but without the reference to reduced live loads? Thinking about it logically, if I reduced the roof live load, it would make sense that the skip loading should be looked into because the skip loading can control the design and where you have reduced the live loads to lower than the 20 psf, it becomes even more critical. But if you don't reduce the roof live load then you can ignore the pattern loading because you have designed for the higher load. Am I interpreting this incorrectly? Applying the roof skip loading can make huge difference. Where snow loads are concerned, skip loading is a must because of drifting, etc. Bur for just roof live load it seems like it isn't necessarily required in the building code.
 
Replies continue below

Recommended for you

But if you don't reduce the roof live load then you can ignore the pattern loading because you have designed for the higher load. Am I interpreting this incorrectly?

Yes - simply use skip loading if you reduce Roof LIVE LOADS.
If you don't reduce the live load below 20 psf, then you don't have to skip the Roof Live Loads.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
JAE,
Does this also apply to cantilevers? Or are cantilevers a little different? I feel that it should be the same.
 
The cantilever moment and shear are unaffected by skip loading but the cantilever - loaded or unloaded - will affect the interior spans.
I always include the cantilever as though it was just another span in my skip loadings.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
JAE,
But for cantilevers do you also only do skip loading if you have reduced the live loading just like multiple spans? Or do you run skip loading on cantilevers even with unreduced live loading?
 
Only with reduced roof live loads.

Check out Eng-Tips Forum's Policies here:
faq731-376
 