Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

How to Wire a FT Switch in a Delta Connected CTs?

Status
Not open for further replies.

Kiribanda

Electrical
May 6, 2003
701
Gentlemen,
Appreciate inputs on the following CT isolation issue.
During electromechanical relay time, the CTs in the wye side of any Dyn transformer were connected in delta (delta side wye connected) and wired to the interposing CTs. Since there is no common wire available for this delta connected CTs,how the FT isolation switch was wired to isolate & ground any CT? In other words in a delta connected set of CTs is grounding necessary? A typical 3-line diagram will be very helpful.
 
Replies continue below

Recommended for you

Grounding is certainly necessary, but that has nothing to do with the FT switch.
 
Thank you very much JG2828.It was the one I was expecting.
 