nan21
Mechanical
- Feb 5, 2017
- 2
Motor Details : 1200 kW @ 3000 rpm with sleeve bearing (proximity probes mounted on bearing)
Observation :
Offline Casing vibration monitoring system:
1) Observed overall vibration readings are on higher side 4.4 mm/sec peak.
2) Dominant vibration observed at 2X CPM (2.80 mm/sec peak) & multiples of shaft running speed.
3) After loosening the bolt, casing vibration drop down to 2.5 mm/sec peak.
4) Vibration varies from 3.5 to 4.4 mm/sec peak.
Online (Bently Nevada) vibration monitoring system:
1) Observed radial vibration readings are on higher side i.e. 80 to 85 micron pk-pk (Y probe showing high vibration as compared with X probe on both bearings).
2) Dominant vibration observed at 1X CPM & multiples of shaft speed.
3) Also during loosening the bolts, radial vibrations are drop to 65 micron pk-pk.
4) Observed orbit shape is elliptical.
5) Vibration observed at slow roll speed is less than 20 micron pk-pk.
As per my opinion, i suggest that to check blue matching for rectification of motor soft foot.
What are other sources of vibration?
Observation :
Offline Casing vibration monitoring system:
1) Observed overall vibration readings are on higher side 4.4 mm/sec peak.
2) Dominant vibration observed at 2X CPM (2.80 mm/sec peak) & multiples of shaft running speed.
3) After loosening the bolt, casing vibration drop down to 2.5 mm/sec peak.
4) Vibration varies from 3.5 to 4.4 mm/sec peak.
Online (Bently Nevada) vibration monitoring system:
1) Observed radial vibration readings are on higher side i.e. 80 to 85 micron pk-pk (Y probe showing high vibration as compared with X probe on both bearings).
2) Dominant vibration observed at 1X CPM & multiples of shaft speed.
3) Also during loosening the bolts, radial vibrations are drop to 65 micron pk-pk.
4) Observed orbit shape is elliptical.
5) Vibration observed at slow roll speed is less than 20 micron pk-pk.
As per my opinion, i suggest that to check blue matching for rectification of motor soft foot.
What are other sources of vibration?