Hi Please refer to attached pdf. C

Status
Not open for further replies.

hhhansen

Electrical
Jan 14, 2004
61
Hi
Please refer to attached pdf. Can anyone tell me what is wrong considering my calculation of U2 potential when there is a single phase fault on HV in secondary substation. I am considering a TT-system with RE and RB not connected.

IEC 60364-4-442 table 44.A1 says U2=U0, however I reach the result U2=U0+(2x RE x IE).

Best Regards

hhhansen
 
 https://files.engineering.com/getfile.aspx?folder=265839f1-4231-4ef0-9ba5-5d308e54b51c&file=IEC60364_table44A1.pdf
Replies continue below

Recommended for you

U0 is the potential between L1 and N, PEN

a_z33lfe.jpg


a_bdw4rh.jpg


So the potential on the HV cabinet at a short circuit is UE = IE* RE
so U1 = IE* RE+ U0
And the potential U2 when RE and RB are not connected is the same as U0.

Best Regard A
 