EngAP
Mechanical
- Jun 6, 2007
- 52
Dear all,
I have calculated the predicted heat loss from a sealed enclosure for various deltaT's (internal temperature to external temperature) using Fourier's Law and achieved reasonable accuracy, even when assuming to be through a straight wall rather than from an enclosure. The theory was confirmed by measuring average internal and external temperatures compared to the heat input.
I then ran physical tests, heating the internal air to set temperatures and measuring the rate of cooling to confirm my theory. But I am getting strange results.
Assuming 0.004 Kg air (m).
Specific heat (Cp): 1005 J/Kg.K
Delta T (initial temp at time = 0 to final temp at time = 100 seconds): 10K
t (time) = 100 secs
Therefore heat removed = Q = m.Cp.deltaT = 0.004 * 1005 * 10 = 40 Joules.
Therefore the avaerage heat flux during the 100 seconds should be Q/t = 40/100 = 0.4W. But this is a lot lower than I was expecting.
If anyone has any ideas or suggestions where I may have gone wrong (in calculation, assumptions etc.) I would love to know.
Note that an internal fan spread the heat as much as possible to achieve an even internal temperature.
Grateful for any advice.
I have calculated the predicted heat loss from a sealed enclosure for various deltaT's (internal temperature to external temperature) using Fourier's Law and achieved reasonable accuracy, even when assuming to be through a straight wall rather than from an enclosure. The theory was confirmed by measuring average internal and external temperatures compared to the heat input.
I then ran physical tests, heating the internal air to set temperatures and measuring the rate of cooling to confirm my theory. But I am getting strange results.
Assuming 0.004 Kg air (m).
Specific heat (Cp): 1005 J/Kg.K
Delta T (initial temp at time = 0 to final temp at time = 100 seconds): 10K
t (time) = 100 secs
Therefore heat removed = Q = m.Cp.deltaT = 0.004 * 1005 * 10 = 40 Joules.
Therefore the avaerage heat flux during the 100 seconds should be Q/t = 40/100 = 0.4W. But this is a lot lower than I was expecting.
If anyone has any ideas or suggestions where I may have gone wrong (in calculation, assumptions etc.) I would love to know.
Note that an internal fan spread the heat as much as possible to achieve an even internal temperature.
Grateful for any advice.