Grounding ATS for Entire Bldg

Status
Not open for further replies.

WoodrowJWeen

Electrical
Jul 30, 2003
112
Adding a generator to serve the entire load of a building. The intent is to intercept the underground service (multiple sets of 3 hots & grounded neutral in PVC ductbank) between the utility padmount transformer and the switchboard inside the building and install an ATS oudoors. This ATS will have a weatherproof enclosure and an integral breaker on the normal side. Does the ATS now become a “service”, requiring the neutral to be connected to ground at this point? If so, then the existing service conductors now are lacking a separate ground wire and not practical to add one. Or, can the “service point” still be considered to be in the existing switchboard allowing the 4 wire service to remain as is and having no neutral to ground connection at the ATS. The existing switchboard is 480Y/277V and over 1000A so it does have GFP on main breaker.
 
Replies continue below

Recommended for you

Nope, your new ATS is your new service. Anyway it is if the NEC is your governing code.
 