cuhead
Electrical
- Oct 20, 2006
- 11
I am trying to solve a grounding issue. I have an ATS in down town LA that is burning up and needs to be replaced right now. The existing ATS is internal to the switchgear lineup and the customer would prefer to replace it with an iso-bypass type to mitigate this exposure in the future. The existing ATS is rated at 4000A and the current load was recorded at 2,500A. I would like to install the new switch 25’ away but the feeders will have to be installed through a DWP (Department of Water and Power) transformer vault ventilation system shaft. I believe that shaft would be classified a plenum. I wanted to install cable tray and use DLO in free air but that is out of the question if it is considered a plenum shaft. Due to the time constrictions I will have to install 9 sets of 4” EMT with 3 RHW-2 646kcmil DLO conductors in each (40C with 90C termination crimp on lugs. I need the DLO for flexibility at the termination.). I will not be able to install a grounding conductor (500kcmil for 4000A) inside each raceway and I cannot correctly bond the conduits with ground bushings because the largest conductor that the bushing will accept is a 4/0. If I classify the EMT as a “grounding conductor” (NEC 250.118) does each EMT equal the 500kcmil required for the 4000A OCPD?