Hello,
I have 14.24 MVA rated synchronous generator driven by gas turbine and it is rated at 42 degree C and all parameters are given based on this temperature.
If this generator will be running at 0 degree C. of site ambient temperature, the generator can cover more kVA e.g. let say 16 MVA as an example.
I think I should use the maximum possible generator MVA at lowest site ambient temperature (e.g. 16 MVA at 0 degree C.) for short circuit current calculation. If so, how about generator parameters? I guess reactance values (X"d, X'd, Xd, etc.) would stay at the same values regardless of ambient temperature, but resistance values (Ra, etc.) would be slightly lower than that of 42 degree C. This would affect generator X/R ratio for short circuit current.
If so, do you think I can use the following equation used for cable resistnace correction?
R’ = R ( 234.5 + Tc )/( 234.5 + Tb )
R = 0.00213 p.u.
Tb = 42 deg.C
Tc = 0 deg. C
R' = 0.001806 p.u. (corrected at 0 deg.C)
This will increase generator X/R ratio and DC component value of short circuit current.
Would you guys please give me advices whether my approaches are appropriate for the maximum short circuit current calculation?
Thanks in advance.
I have 14.24 MVA rated synchronous generator driven by gas turbine and it is rated at 42 degree C and all parameters are given based on this temperature.
If this generator will be running at 0 degree C. of site ambient temperature, the generator can cover more kVA e.g. let say 16 MVA as an example.
I think I should use the maximum possible generator MVA at lowest site ambient temperature (e.g. 16 MVA at 0 degree C.) for short circuit current calculation. If so, how about generator parameters? I guess reactance values (X"d, X'd, Xd, etc.) would stay at the same values regardless of ambient temperature, but resistance values (Ra, etc.) would be slightly lower than that of 42 degree C. This would affect generator X/R ratio for short circuit current.
If so, do you think I can use the following equation used for cable resistnace correction?
R’ = R ( 234.5 + Tc )/( 234.5 + Tb )
R = 0.00213 p.u.
Tb = 42 deg.C
Tc = 0 deg. C
R' = 0.001806 p.u. (corrected at 0 deg.C)
This will increase generator X/R ratio and DC component value of short circuit current.
Would you guys please give me advices whether my approaches are appropriate for the maximum short circuit current calculation?
Thanks in advance.