Sweever
Structural
- Sep 13, 2017
- 29
I am analyzing whether a new generator pad is required for a 26,000lb (wet weight) generator. I have read the other post on this subject, however mine situation is somewhat different. The existing slab is 30' x 20' x min. 9" thick, and is founded directly on rock. This pad currently houses 3 generators and one is going to be replaced. Going through the manufacturer design data, they are recommending a concrete mass equal to 2 times the wet weight of the unit and based on the manufacturers foundation thickness equation (foundation depth = Weight/ (density of concrete*width* length of foundation), I need a min. 3 foot thick slab. The existing 9" slab is reinforced with 2 layers (T&B) of #4 bars each way and is anchored to the existing rock with 15-#4 vertical dowels grouted into the rock 9" and extending into the slab 6".
I don't know the capacity of the of the rock, but would assume 21,000psf at a minimum so bearing capacity is not a concern. The new generator is on vibration dampers (8)
My question would be how to know if the existing dowels are suitable to mobilize the mass of the rock below?
Thanks
I don't know the capacity of the of the rock, but would assume 21,000psf at a minimum so bearing capacity is not a concern. The new generator is on vibration dampers (8)
My question would be how to know if the existing dowels are suitable to mobilize the mass of the rock below?