jamesbanda
Chemical
- Sep 21, 2004
- 223
The purpose of this question is to understand partices used for operating pressure Management of change and relief load evaluations.
For a gas filled vessel the relief rate / ultimate pressure rise depends on the start pressure (e.g.) how much gas is present at the start. So. From a relief sizing perspective, if you have a higher start pressure the relief valve will be larger.
So, what is the convention that users are deploying for the start pressure.
a) Max, normal operating pressrue (high alarm)
b) Software based trip
c) Hardwired based trip.
Clearly, if the trip point is used the relief valve is larger but more management of change is considers prior to changing this than an operating point. If an operating point is selected one could unknowingly change the operating pressure without knowing and find the relief valve is undersized.