is there any problem if I fit the nozzle flame arrestor on center roof tank?, then what is the better location
 
Replies continue below

Recommended for you

Which way is the flame front travelling? Towards the tank from a pipe, or from inside the tank out a pipe?

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
I would recommend talking to these guys.


Note: I am not a representative, and do not have an interest in Enardo.

"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376 to make the best use of Eng-Tips Forums?
 
Note that API-2000 has a statement saying you don't need a flame arrestor if you have a P/V vent.
 
Flame arrestors can ice up and prevent the P/V vent from working properly, leading to tank collapse inwards when you withdraw liquid.
 