BVMan
Mechanical
- Jun 20, 2003
- 27
We have recently carried out a Fire Test on Behalf of a Client on a 'Stock' 2" ANSI 150RF Wedge Gate Valve. Around half way through the burn period there was a 'Pop', the Stem Thermocouple dropped slightly and there was a slight 'Roar' from the fire. The Pressure remained constant and temperatures recovered, without dipping below the required minimum, allowing the full burn to be completed. However, after cooling there was a significant leakage from the bonnet joint which resulted in the valve failing the test.
On post test examination the 304/Graphite Oval Spiral Wound Bonnet Gasket (Flat Faced - Non encapsulated) was found to have failed and the bonnet bolting (B7M/2HM) required only low torque to unfasten.
It seems that the Seating functioned quite well but the failure was due to trapped water in the Bonnet area vaporising. We had not fitted a Relief Valve/Gauge to the bonnet so cannot confirm that this was the case.
My issue is that even if out assumption is correct and a Relief Device were fitted and opens during the test this would result in the test being aborted. Meaning that if the valve seats function correctly during the burn the fluid trapped in the bonnet will expand resulting in either failure of the Packing or Gasket, or where fitted the Relief device will operate, either way the Valve Fails.
Obviously a Cavity Relief Hole in the Wedge is one option but this makes the Valve uni-directional and there is no evidence of other manufacturers going down this route. I have seen test reports stating that the Valve Seats were completely destroyed but the drawings state that the seats tested were A105 + Hardfacing.
Does anyone have any experience, thoughts or comments?
On post test examination the 304/Graphite Oval Spiral Wound Bonnet Gasket (Flat Faced - Non encapsulated) was found to have failed and the bonnet bolting (B7M/2HM) required only low torque to unfasten.
It seems that the Seating functioned quite well but the failure was due to trapped water in the Bonnet area vaporising. We had not fitted a Relief Valve/Gauge to the bonnet so cannot confirm that this was the case.
My issue is that even if out assumption is correct and a Relief Device were fitted and opens during the test this would result in the test being aborted. Meaning that if the valve seats function correctly during the burn the fluid trapped in the bonnet will expand resulting in either failure of the Packing or Gasket, or where fitted the Relief device will operate, either way the Valve Fails.
Obviously a Cavity Relief Hole in the Wedge is one option but this makes the Valve uni-directional and there is no evidence of other manufacturers going down this route. I have seen test reports stating that the Valve Seats were completely destroyed but the drawings state that the seats tested were A105 + Hardfacing.
Does anyone have any experience, thoughts or comments?