This is an issue that confounds me and others I have talked with but has very little exposure and as far as I can tell no recognition in the codes.
I came across this the in the forum "thread407-292211"
In our case we have found extensive damage to the intake of the pumps around the wear ring as well as severe erosion of the vanes in the pumps (flow diverts, cut-waters, it seems there are a number of names for the 90 degree devices sticking out into the flow).
In the thread the comment was that it was stupid to run the pump when you did not have to.
You are obligated (though often not done) to run these 30 minutes a week (diesels).
In our case, we are also obligated to maintain protection and if we dump water (and winter is impossible) we are creating an impairment to the building we are supposed to be protection.
If it was mandated that at minimum there be a recirculation loops (with a flow meter so you can determine what your flow is) that would prevent it. Better yet would be a line back to the tank.
With the damage to the pumps and no viable solution you have to repair if possible and then replace expensive pumps. That should not take place. My take is no pump MFG wants to say his pump needs to recirculate and others not say anything and put themselves at a competitive disadvantage (read that no pump sales)
I talked to an engineer who formally had a job where he tested and repaired systems. His comment was that most of the systems he worked on had issues.
Its hard to see as the deterioration is slow and the system still meets the NFPA specs, but if actually compared to the original test cures you can see the degradation and in fact its tearing itself apart inside.
I think this subject should have a lot more discussion and exposure. I see the committees meeting a coming up with all sorts of nit noid updates when there are serious issues that are not addressed.
I came across this the in the forum "thread407-292211"
In our case we have found extensive damage to the intake of the pumps around the wear ring as well as severe erosion of the vanes in the pumps (flow diverts, cut-waters, it seems there are a number of names for the 90 degree devices sticking out into the flow).
In the thread the comment was that it was stupid to run the pump when you did not have to.
You are obligated (though often not done) to run these 30 minutes a week (diesels).
In our case, we are also obligated to maintain protection and if we dump water (and winter is impossible) we are creating an impairment to the building we are supposed to be protection.
If it was mandated that at minimum there be a recirculation loops (with a flow meter so you can determine what your flow is) that would prevent it. Better yet would be a line back to the tank.
With the damage to the pumps and no viable solution you have to repair if possible and then replace expensive pumps. That should not take place. My take is no pump MFG wants to say his pump needs to recirculate and others not say anything and put themselves at a competitive disadvantage (read that no pump sales)
I talked to an engineer who formally had a job where he tested and repaired systems. His comment was that most of the systems he worked on had issues.
Its hard to see as the deterioration is slow and the system still meets the NFPA specs, but if actually compared to the original test cures you can see the degradation and in fact its tearing itself apart inside.
I think this subject should have a lot more discussion and exposure. I see the committees meeting a coming up with all sorts of nit noid updates when there are serious issues that are not addressed.