Help me out. I’m a bit confused. We build industrial control panels for industrial machinery per UL508a. We use an instantaneous circuit breaker as the machine/panel disconnect. The current panel I am designing has two 30HP motors, one 0.5HP motor, and a 500VA control transformer. All of the motor branches use Type E self protected starters.
Here is where I am confused. The code states that the disconnect can not be sized for more than 80% of it’s rating. I’ve had to bump up to a 150A disconnect. The FLA on the panel is 94A. I’ve multiplied the two 30HP motors by 125% due to our machines being designed to use service factor during part of the process. Do I size the wire from the bottom of the breaker to the distribution block based on the FLA (94A) or do I size it for the size of the breaker (150A)? Could this be considered feeder protection as well as disconnecting or will the customer need to supply feeder protection in the field?
Here is where I am confused. The code states that the disconnect can not be sized for more than 80% of it’s rating. I’ve had to bump up to a 150A disconnect. The FLA on the panel is 94A. I’ve multiplied the two 30HP motors by 125% due to our machines being designed to use service factor during part of the process. Do I size the wire from the bottom of the breaker to the distribution block based on the FLA (94A) or do I size it for the size of the breaker (150A)? Could this be considered feeder protection as well as disconnecting or will the customer need to supply feeder protection in the field?