chileheadcraig
Civil/Environmental
- Nov 15, 2002
- 50
I work for a water utility and we have a conundrum that none of us can figure out. One of our zones is a pump station/water tank fed setup where water going to the distribution system is controlled by tank level. While a typical setup would consist of a pump station being tripped on and off by tank level, our setup is a bit different and I'll try to explain as best as I can as follows:
We have a VFD pump station which maintains a constant pressure our water plant that provides both plant water and serves a portion of our system by filling a reservoir. The pump station needs to run 100% of the time to provide plant water, so delivery to the distribution system is controlled by a valve. When the tank reaches 'low', the valve at the plant opens and allows the tank to fill. When its full, the valve closes and the zone is fed by the tank. Similar setup as a standard pump on/off scenario but instead its a valve open/close.
The problem is, when the valve closes (and is no longer fed from the PS), the pressure drops from about 90 psi to 20 psi (or less) and takes about 30 seconds to recover to normal pressures (being totally tank fed). The tank is located pretty central in the zone and the pump station is at the southern end. The pressure drop is only seen in the area between the pump station and tank. All areas north of the tank are isolated from the phenomena and continue to get fed from the tank, as expected. The valve closes from 75% open to closed over a period of 2 minutes, so its not slamming shut, so transients do not seem to be the culprit.
Any idea whats causing this pressure drop and slow recovery? Why would the reservoir not simply take over and feed the area to the south? We have checked the check and altitude valves at the reservoir and all isolation valves on the line from the tank back to the plant and have ruled out issues there.
Attached are several events from our Telog pressure recorder, which samples at high frequency. The pattern appear like clockwork every time. Thanks for any feedback or ideas.
We have a VFD pump station which maintains a constant pressure our water plant that provides both plant water and serves a portion of our system by filling a reservoir. The pump station needs to run 100% of the time to provide plant water, so delivery to the distribution system is controlled by a valve. When the tank reaches 'low', the valve at the plant opens and allows the tank to fill. When its full, the valve closes and the zone is fed by the tank. Similar setup as a standard pump on/off scenario but instead its a valve open/close.
The problem is, when the valve closes (and is no longer fed from the PS), the pressure drops from about 90 psi to 20 psi (or less) and takes about 30 seconds to recover to normal pressures (being totally tank fed). The tank is located pretty central in the zone and the pump station is at the southern end. The pressure drop is only seen in the area between the pump station and tank. All areas north of the tank are isolated from the phenomena and continue to get fed from the tank, as expected. The valve closes from 75% open to closed over a period of 2 minutes, so its not slamming shut, so transients do not seem to be the culprit.
Any idea whats causing this pressure drop and slow recovery? Why would the reservoir not simply take over and feed the area to the south? We have checked the check and altitude valves at the reservoir and all isolation valves on the line from the tank back to the plant and have ruled out issues there.
Attached are several events from our Telog pressure recorder, which samples at high frequency. The pattern appear like clockwork every time. Thanks for any feedback or ideas.