Energy usage calculations of heat exchanger 1

Status
Not open for further replies.

wilsonudevil

Mechanical
Jun 8, 2009
2
Hi all,

I'm trying to calculate the energy usage of a developmental hybrid ventilation system.

It's a small domestic sized unit with a water/air heat exchanger. Fresh air from outside flows through the unit where it is tempered before entering a room.

I've rigged it up so that air is blowing over the heat ex at 40 l/s. Warm water is flowing through the heat ex at 4 l/min in a closed loop. I'm heating the water with a domestic immersion heater with an energy meter attached to it.

Letting the system stabilise and then run for an hour, if I use Q=mCpDT to calc the energy given to the air crossing the heat ex it is always much higher than the experimental reading I take from the energy used by the water heater. I thought it would be the other way around! I'm pretty sure my flow rates are correct.

Any ideas?

Many thanks.
 
Replies continue below

Recommended for you

Did you include pump heat, fan heat and thermal loss of sheet metal and ductwork. Run the calculations with the +/- accuracy of the air flow meter and temperature sensors. How did you measure electric heat input to the immersion heater (true watts)?
 
I didn't include pump heat so that will contribute. Thanks!

Thermal losses through ductwork etc should act to increase my energy reading shouldn't they?

I measured the electric heat input using a cheap off-the-shelf power meter, but have checked it using a commercial unit and it's actually quite accurate. What's 'true watts'?
 
Your KWH meter should be certified to a known standard such as ANSI C12.1 and C12.16 Electronic Meter National Accuracy Standards. You then can project the accuracy (%) of the readings.
 
Cp of water changes with temperature but this is a relatively small factor. The flow rate is the only thing that could get you far from the mark. How many watts are the pump and the heater?
 