Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Electrical Isolation for natural gas piping

Status
Not open for further replies.

gatman

Mechanical
Oct 12, 1999
2
The 1997 Uniform Mechanical Code requires electrical isolation for fuel gas piping (paragraph 1312.7). What fittings are listed or approved for fuel gas service that are capable of electrically isolating natural gas piping? The piping I am concerned about is black iron, threaded, 3/4" to 2" in diameter. The pressures are low, 5-15 psig.<br>
<br>
Is there an authority that has approved dielectric unions for this service? I have been looking for an answer to this problem for a month and have come up empty. The local gas companies use isolation fittings as a standard practice, but that is not adequate for the building official I am working with.<br>

 
Replies continue below

Recommended for you

I was able to answer my own question. I contacted Paul Cabot at the American Gas Association. The AGA is an affiliated group of gas companies who are active in development of the NFPA and other codes. Very much like a professional organization such as ASHRAE or ASME.<br>
<br>
Mr. Cabot tells me there are no listed fittings for natural gas service. He also tells me gas companies use dielectric unions and isolation flanges as standard practice.<br>
<br>
The testimony of Mr. Cabot along with catalog cut sheets from the local gas companies should be enough to convince the mechanical inspector of thier validity.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor