Derivation of First Storey Shear Rigidity for a Rigid Frame
Scotty Boy
7
I am wondering if anyone is familiar with any of Bryan Stafford-Smith and Alexander Coull's work?
I have their book Tall Building Structures, Analysis and Design.
For rigid frames they express an parameter for the racking stiffness called the shear rigidity (GA).
For intermediate storeys they give the shear rigidity as:
GA = Qh/delta
Where:
Q = the storey shear
h = storey height
delta = the lateral deflection
To calculate delta the points of contraflexure are assumed to be mid-storey height. From this we get the deflection due to column flexure as Qh^2/(12*E*C), and the deflection due to girder flexure as Qh^2/(12*E*G).
Where:
C = Ic/h
G = Ig/L
Substituting this into GA
GA = Qh/(Qh^2/12E) (1/C + 1/G)
Which gives:
GA = 12E/(h(1/C + 1/G)
A quite simple derivation I think.
Now, because it is inaccurate to assume points of contraflexure at mid height for the bottom storeys, Stafford-Smith and Coull provide a tweaked equation for the shear rigidity. It comes in the form:
GA = 12E(1 + C/2G)/(h[1/C + 2/3G])
Unfortunately, they don't give a derivation for this, and I need to know this. Does anyone know how to derive it? I assume that they have taken the points of contraflexure as 2/3 from the base.
Here is the page from the book that shows how they derive the shear rigidity for the intermediate storeys.
The diagrams demonstrate the joint rotation due to girder flexure, the storey drift due girder flexure, and storey drift due to column flexure respectively.
If you need any more information, please ask.
Thanks.
Are we all clueless on this?
I have more than clue .. trying to remember.
My points ;
- Your expression GA = 12E/(h(1/C + 1/G) apparently covers girder flexure and column flexure . For total drift, you need to add story drift due to overall bending.
- The first floor ( also top floor ) differs . The point of contraflexure no more at h/2, for first and top floors,
- For the first floor , assume the column is fixed to the foundation ( rigid base conn.) then calculate the rotational stiffness .
It is strange for me that , your question is for approximate methods of 50 yrs ago. Probably you are asking just for curiosity.
Nowadays , with high-speed computers, and enhanced softwares no need to use approximate methods.
Great! I am very glad you have a clue! :)
I'm glad you mentioned that about the top storey, because I want to derive the expression for GA in the top storey. The point of contraflexure, from my observations, can be a as small as 1/4 the length of the column (going upwards) for the top storey. If I can work out how Stafford-Smith and Coull derived the GA for the bottom storey, I can hopefully derive it for the top storey.
You says about the rotational stiffness - is this not just 6EI/h^2?
If you could help me further (maybe with some steps) I would really appreciate it.
Thanks, HTURKAK.
Are you there, HTURKAK?
Yes .. I am here now. I do not look to the forum everyday .
Regarding your questions,
No not in this case.
Rotational stiffness of the beams ( say picture you have posted , b and c) ; 12E* ( SUM OF Ib/ Li)
Steps for the extraction of expression GA = 12E(1 + C/2G)/(h[1/C + 2/3G]), could be ,
- The proposed expression is for an assumption applicable for certain spans / depth ratios , beam column stiffness ratios. I assumed the span and height are the same, inertias are the same , for this assumptions the point of contraflexure is 4h/7 from bottom.
- Assume a frame ( say figure C in your post ) with the dimensions conforming the assumptions ,
- Apply a unit horizontal displacement and find the relevant moments using moment distribution / Cross method for the fixed base and joint , then find the height of contraflexure ,
- Calculate the story drift for beam and columns ,
- Then extract the shear rigidity
You may also try to use inverse calculation .
Your question reminded me a film poster from 1983 Star Wars . Fighting with stone axe at one hand and laser weapon at the other hand.
My opinion.
- Apply a unit deflection and find the relevant moments using moment distribution / Cross method for the fixed base and joint , then find the height of contraflexure
Would it be possible for you to demonstrate this with some numbers - E, G, C, Q, h, L etc? Because even though I have some experience using the moment distribution method for beams, I am unsure how to apply it in this case.
I like to learn how to use the stone axe, because it helps me learn the behaviour of structures :). Also, isn't there a phenomenon called Computer Aided Disaster?