Derating Cables

Status
Not open for further replies.

SparkyLarks

Electrical
Jul 14, 2005
43
I have an application in the UK where a 3.3kV AWA cable is being installed. The Length is 250m total and most is being installed in a Cable tunnel or outside on tray, but the Last 14m passes through a duct.

The Max current is 560A.( this would assume that 2 normally open points have been closed on the LV system. The normal current Max would be 230A

400sqmm cable when installed in duct has a current rating of 535A. (The rating in the trench is approx 840A x .8)
We have increased the size requirement to 500sqmm.

However my question is a general one. Is there any length of duct at which you would ignore it when cable sizing?
 
Replies continue below

Recommended for you

In the USA, the National Electrical Code has an exception if the distance is less than 3 m or 10% of the circuit length, whichever is less.
 