SparkyLarks
Electrical
- Jul 14, 2005
- 43
I have an application in the UK where a 3.3kV AWA cable is being installed. The Length is 250m total and most is being installed in a Cable tunnel or outside on tray, but the Last 14m passes through a duct.
The Max current is 560A.( this would assume that 2 normally open points have been closed on the LV system. The normal current Max would be 230A
400sqmm cable when installed in duct has a current rating of 535A. (The rating in the trench is approx 840A x .8)
We have increased the size requirement to 500sqmm.
However my question is a general one. Is there any length of duct at which you would ignore it when cable sizing?
The Max current is 560A.( this would assume that 2 normally open points have been closed on the LV system. The normal current Max would be 230A
400sqmm cable when installed in duct has a current rating of 535A. (The rating in the trench is approx 840A x .8)
We have increased the size requirement to 500sqmm.
However my question is a general one. Is there any length of duct at which you would ignore it when cable sizing?