Cold Formed Steel Ledger Connection @ Loft Infill/Platform 1

Status
Not open for further replies.

FoxSE14

Structural
Feb 5, 2011
131
I am designing a new cold formed steel loft to be constructed within the confines of existing wood stud walls, so I have a ledger condition along the perimeter. I am sure this has been tackled before using CFS, but I am having a tough time quickly finding a typical approach to this detail. My concern with using a CFS member as the ledger lies in the local effects (warping, fastener tearing/pullout, etc). If forced into CFS ledgers, I personally would gain some comfort by doubling up the ledger member and drive the fasteners through the nested webs, possibly adding stiffeners/some connection to tie the top & bot flanges. Any CFS experts out there?

On the attached sketches, I prefer approach #2 for both the "joist perpendicular" and "joist parallel conditions" (biggest driver is my limited experience using CFS and preference toward wood). I'll be dumping approximately 400# at the joist perpendicular connection. Is it so crazy to have a CFS contractor cut a few wood ledgers? Seems reasonable to me.

Our office has limited experience with CFS, so, I welcome any input/feedback - thanks in advance!
 
 http://files.engineering.com/getfile.aspx?folder=a70fc2fc-9f71-4f6d-b51c-fbd3b1255b3e&file=CFS_-_Loft_Infill.pdf
Replies continue below

Recommended for you

Check out the Simpson cold formed connectors. They have quite a few connectors for cold formed steel to wood or vice versa. It may help simplify your detailing some.
 
This too: Link

My gut sense is that you want option #1, single ply, no flange to flange stiffeners. It looks conventional and reduces eccentricity. I feel your pain though. Hybrid connections are always a pain.

I'm going to mentally summon XR250 to your thread for you... now! He's a wiz at this stuff as he does specialty work in CFM.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Thanks Mike - I took a look at that publication and it gave me the idea for the SJC and S/JCT connector shown in my sketch. Have you, or anyone else, specified anything similar to the ledgers I showed? Or have you gone a different/more creative direction entirely?
 
For option #1, I was thinking that the joists would actually be nested into the track.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Thanks KootK -- wow, you're over my shoulder -- I am browsing the same document as some frantic googling led me to the same within the last hour or so! Great reference that I'll be keeping for future CFS projects.
 
KootK - yep I follow. The only reason I went away from that is because I was thinking that I want lips on the ledger since it may need to span between existing studs (although, with wood backup studs at just 16", perhaps I am overthinking and a traditional "lipless" track will suffice). Can you tell I normally don't deal with CFS? [roll1]
 
I like option one for joists perp. and either option for joists parallel.
What is the joist span, design loads and are the joists intended to brace the walls?
 
Joist span is 11.5', say 12psf DL & 40 psf LL. Joists are not intended to brace the walls (walls are part of existing residence).

XR - thanks. I am leaning toward modifying my approach to choice 1 for joists perp by doing something similar to what KootK suggested, i.e.: use a typical track ledger and avoid eccentricity that the Simpson SJC is imposing. Any opinion on that?
 
I typically use the track as a ledger for 8" joists even though I think the CFS spec for designing those maxes out at 6". Your point load is about 400lbs at each joist. I would not worry about using a 16ga track and calling it good. Might want to go to a 14" track for giggles. For the parallel case, anything is going to work.
 