Dear Members,
We are a Boiler manufacturer. We have supplied 2 Nos Low Tension motor - 415V; 50Hz 0f 110 Kw for fan application. Each fan is having full load capacity. The first fan is with VFD and the second is with star/delta starting and inlet regulating vane flow control. The boiler was commissioned and operating for some days with first fan. Then they have started second fan. After running far a day with some load, the motor winding got burned. The motor was opened out for analising the cause of burning. It was noted that there was rubbing of stator and rotor winding on the NDE side. The motor manufacturer rewound the same motor and sent to the project. The motor was meggered which was 5 Mohm plus. Run on no load for a day and then coupled to the fan. After running for just 90min., the motor burnt once again. Opening of motor indicates same rubbing of stator and rotor winding on the NDE side.
There was no specific additional noise noted during both failures.
The coupling of fan and motor is standard flexible coupling.
The control circuit is provided with thermal over load relay for over load protection and fuses for short circuit/earth fault protection. We have also provided single phase preventor across the power fuses.
During both occassions, the voltage was normal and current taken were within limits.
Customer is now asking for a new motor and not once again rewing the motor. The motor manufacturer was telling the failure of motor was due to fan problem only which we have disputed as the rubbing was noted in the nondrving end.
I request the fourum can discuss on cause and remedy for the above problem.
Regards,
R.Thiyagarajan.