Hi all,
I came out with this interesting thought. Say I have a braced frame isolated footing which will take 300 kips seismic lateral shear (footing takes all lateral shear, no slab on grade involved). My question is that:
Do we usually consider this 300 kips in the footing design, besides overall frame overtuning?
To be specific, say for example the footing is 42" deep, do we consider the extra 1050 k-ft (300x42/12) moment in the soil bearing pressure design check for this footing? The extra soil pressure will be 1050 k-ft / (bh^2/6) if no uplift, with b the width and h the length.