The more I study the possiblities the more uncertain I become about what to use. We are doing an estimate for a chemical process plant where Foundation Fieldbus(FF) has been decided for use with Analog - Transmitters and Positioners.
The question is what to do with the on-off valves and switches? My first impression was that FF would be overkill and unecessarily expensive. I then moved to the Profibus world. It seemed to be very similar on the hardware level which I liked. However when I began to look at the availability, the first two common topworks companies I checked (in the US)seemed to only be set up for the high speed version that requires separate power and not the PA version which does not.
This plant is very large with two areas with concentrated process and then many small areas spread way out- a tank half a mile away , wastewater, etc.
The Actuator and topworks people seem to more set up for AS-i bus than anything but I was shying away from it because of its length limitations -100 meters(300 meters with repeaters).
I've received some component prices and was surprised to learn that profibus topworks were not much less expensive than FF.
We are expanding an existing ABB DCS system and I really hate the idea of having FF for analog and back to the wire-everything-standard I/O for the discrete stuff.
If anyone has gone through this and can give me some conclusions you reached , I would much appreciate it.
The question is what to do with the on-off valves and switches? My first impression was that FF would be overkill and unecessarily expensive. I then moved to the Profibus world. It seemed to be very similar on the hardware level which I liked. However when I began to look at the availability, the first two common topworks companies I checked (in the US)seemed to only be set up for the high speed version that requires separate power and not the PA version which does not.
This plant is very large with two areas with concentrated process and then many small areas spread way out- a tank half a mile away , wastewater, etc.
The Actuator and topworks people seem to more set up for AS-i bus than anything but I was shying away from it because of its length limitations -100 meters(300 meters with repeaters).
I've received some component prices and was surprised to learn that profibus topworks were not much less expensive than FF.
We are expanding an existing ABB DCS system and I really hate the idea of having FF for analog and back to the wire-everything-standard I/O for the discrete stuff.
If anyone has gone through this and can give me some conclusions you reached , I would much appreciate it.