EBF
Structural
- Jun 2, 2003
- 62
According to 2002 AISC Seismic Provisions, Sec. 11.2(1) FR moment connections need to be designed for the flexural strength of the beam defined as 1.1RyMp. I am using a WUF-W connection (FEMA 350 Sec 3.5.2), which has the beam flanges welded directly to the column flanges. For the CJP groove weld at the top and bottom flange, the tension capacity is 0.9FyA. How can this requirement be satisfied when the capacity of the weld is equal to the flange tension capacity but the required strength is the beam capacity increased by 1.1Ry? For a W18x 50 beam, 1.1RyMp = 1.1*1.1*50ksi*101in3 = 6110 in-k which results in a flange force of 6110/18in = 340k. The capacity of a CJP groove weld would be 0.9FyA = 0.9*50ksi*7.5in*0.57in = 192k. Please explain where I am going wrong.