alehman
Electrical
- May 23, 1999
- 2,624
We experienced failure of the arresters I mentioned in thread238-213060. The utility feeding this switchgear is 4800V ungrounded with about 21kA sym available. The circuits are from a common substation bus, ungrounded, and do not have recloser operation. I selected an intermediate class polymer 6kV gapless MOV arrester, rated 40KA pressure relief. Their 10kA, 8/20 crest voltage is 16.7kV. They are installed in separate compartments in metal-enclosed interrupter switchgear, rated 15kV.
This is a main-tie-main setup with the arresters in separate back-to-back compartments. The side was blown out of the C-phase arrester on main #2. About 15 minutes later there was a fault in the arrester compartment protecting main#1 and its C-phase arrester was destroyed. I can't tell if the origin of the second fault was internal to the arrester or external. There was considerable arcing in both arrester compartments, but I don't know exactly when it occurred. Fuses on both mains were found blown, but again I don't know exactly when. The utility reported a ground fault for roughly the time interval between our two events.
The utility engineers and local electricians are suggesting a higher voltage rating. The arresters protect oil-insulated transformers rated 60kV BIL that are about 50 feet away.
Any thoughts on changing the arresters to 9 or 10kV ? Any other thoughts on the failures or replacement arresters type selection?
This is a main-tie-main setup with the arresters in separate back-to-back compartments. The side was blown out of the C-phase arrester on main #2. About 15 minutes later there was a fault in the arrester compartment protecting main#1 and its C-phase arrester was destroyed. I can't tell if the origin of the second fault was internal to the arrester or external. There was considerable arcing in both arrester compartments, but I don't know exactly when it occurred. Fuses on both mains were found blown, but again I don't know exactly when. The utility reported a ground fault for roughly the time interval between our two events.
The utility engineers and local electricians are suggesting a higher voltage rating. The arresters protect oil-insulated transformers rated 60kV BIL that are about 50 feet away.
Any thoughts on changing the arresters to 9 or 10kV ? Any other thoughts on the failures or replacement arresters type selection?