Arc-flash on Grounded-B system

Status
Not open for further replies.

SJBatTCE

Electrical
Oct 8, 2001
41
Anyone have suggestions for conducting an arc-flash study on a 480V, three-wire, grounded-b system? Is this possible? If so, should it be treated as an ungrounded-delta? Not sure where to start with this one... TIA!
 
Replies continue below

Recommended for you

SJB

One has a grounded system. Use the grounded fudge factor. Treat it as any other grounded 480 volt system.
 
That's what I'm inclined to do here. My arc-flash numbers will be quite conservative as there will be only two phases contributing to the fault, correct?
 
Nope, it will be a three-phase fault, just like any other arc-flash event.
 