Timoteo811
Structural
- Jan 25, 2011
- 2
Do the ACI load factors depend on the late gain strength of concrete?
Specific question:
Both Field and Labortory test come back below strength at about 85% of fc'(28 day). Testing at 56 days shows that the strenth is about 90% of desing strength.
Knowing that there is still some design strength to be gained and the it is not a construction loading issue the concrete is accepted.
Is this concrete more prone to failure since it did not achieve the design strength at 28 days but rather after 56 days?
Also if cores are used to determine the acceptance of the placed concrete, do I understand it correctly that the samples only need to acheive 85% of the desing value to be "full strength" per ACI?
Specific question:
Both Field and Labortory test come back below strength at about 85% of fc'(28 day). Testing at 56 days shows that the strenth is about 90% of desing strength.
Knowing that there is still some design strength to be gained and the it is not a construction loading issue the concrete is accepted.
Is this concrete more prone to failure since it did not achieve the design strength at 28 days but rather after 56 days?
Also if cores are used to determine the acceptance of the placed concrete, do I understand it correctly that the samples only need to acheive 85% of the desing value to be "full strength" per ACI?