scottiesei

Structural
Mar 16, 2006
176
Can anyone verify if the provisions for lap splices is the same in ACI 530 as it is in ACI 318? I have the current 530 and have seen that they changed from 2002. Have they also changed in 318 from 2002 to 2005?
Thanks in advance!
 
Replies continue below

Recommended for you

Does anyone have a copy of ACI 318-05 that can share the lap splice equation or just verify if it parallels ACI 530?
 
ACI 318-05

Class A splice ............... 1.0 ld
Class B splice ............... 1.3 ld
 
ACI 318-05 development length equations appear to be the same as the 318-02 except they changed the symbols. The resulting lengths should be the same.
 
scottiesei: Are you asking about ACI 530 MSJC? Their lap length for masonry is different from ACI318 for concrete. I did not get a chance to compare them though, but I suspect for masonry the splice length will be longer.
 
rt06, I would agree but if we use the new MSJC equation for a grade 60 #5 bar we still come up with 25" (depending on the cover). I believe 318 would give about 30" say in the bottom of a continuous footing.
 