I have a 45MW 13.8Kv 60HZ Generator with a Brushless Excitation system on it. The Generator is a 3600 rpm two pole machine. There is a PMG (Permanent Magnet Generator) mounted on the end of the Brushless Exciter that puts out 292Vac at 240HZ to a Brush Prismic A30 Automatic Voltage Regulator (AVR). In the manual mode of the AVR we can slowly increase the DC current to the Pilot Exciter field from 0 to 5Adc. That DC current is used to excite four (4) stationary field coils around a shaft mounted 3 phase AC Generator. The AC Generator should produce 3 phsae AC voltage which is then full wave rectified by 6 diodes located on a diode wheel which in turn produces 0 to 350Vdc which is passed through to the Main Generator Field. The nameplate on the Generator indicates that approximately 2.5Adc should be enough to get to full voltage no load.
As the Generator is accelerated to 3600rpm we can see a small amount of residual voltage buildup on the Generator stator. (approximately 50Vac per phase) by watching the Generator Potential Transformer (PTs Open Delta)
As we increase the DC current from the AVR from 0 to 2Adc we see no buildup of voltage on the Generator Stator.
We have checked the diodes and fuses and verified the main Generator field (0.485 ohms) is correct. We have disassembled and reassembled the entire diode wheel and fuses. Is it possible that if the field coils were not connected in the correct polarity it could prevent the shaft mounted AC Gnerator from producing any voltage?
Does anyone have any ideas of any tests I can run to prove the various parts are working?
As the Generator is accelerated to 3600rpm we can see a small amount of residual voltage buildup on the Generator stator. (approximately 50Vac per phase) by watching the Generator Potential Transformer (PTs Open Delta)
As we increase the DC current from the AVR from 0 to 2Adc we see no buildup of voltage on the Generator Stator.
We have checked the diodes and fuses and verified the main Generator field (0.485 ohms) is correct. We have disassembled and reassembled the entire diode wheel and fuses. Is it possible that if the field coils were not connected in the correct polarity it could prevent the shaft mounted AC Gnerator from producing any voltage?
Does anyone have any ideas of any tests I can run to prove the various parts are working?