Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

3 phase disconnect - correct size rating

Status
Not open for further replies.

utimgr

Electrical
Jun 19, 2006
24
In the midst of a discussion with another PM about this....

System is 3 phase, 480VAC, total HP of motors are 28.166 (25,2,.5, 1/3, 1/3) and 42.3FLC (36,3.5,1.2,.8,.8)

I'm saying that we need a disconnect rated at min of 30HP or 45A....he says its 1/3 of that since each phase carries 1/3 of the FLC. Say it enough times and it starts to make sense..but still doesnt sound right. Each leg is out of phase, but still carries the FLC ?
 
Replies continue below

Recommended for you

Each phase carries the full load amps.
 
dpc said it all. You can't say it enough times for it to make sense.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
He must be a politician. Repeat a lie enough times and someone will believe it.

And by the way, 480V and HP ratings implies North America, subject to the NEC or CEC, both of which have specific code requirements for mimum sizing of disconnects for multiple motor loads. I suggest you read them before moving forward, any other course of action is irrelevant until after that minimum is met.


"Will work for salami"
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor