1/3 increase for toe pressures....why?

Status
Not open for further replies.

bigmig

Structural
Aug 8, 2008
401
I was reading a soils report and found the following sentence...

"...A 1/3 increase in allowable bearing pressure can be taken for toe pressure in eccentrically loaded footings"

I have never seen this in a soils report. Where is this 1/3 increase coming from? The report makes no distinction between load type.
 
Replies continue below

Recommended for you

I can think of two possibilities:

1) Many eccentrically loaded footings get their eccentricity of load by way of transient loads such as wind and earthquake. ASD load combinations do -- or at least used to -- allow a 1/3 increase for that. But then, as you suggested, this would be dependent on the load source.

2) For shallow foundations governed by settlement, which is to say most of them, it doesn't make sense to limit bearing capacity to the allowable soil stress at the footing toe where the value is at it's peak. Something closer to the average stress under the footing is a better predictor of settlement. That may be what's happening.