Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by ZDR1985

  1. ZDR1985

    Cooling load calculation method

    Rules of thumb comes with experience. If you are still beginning with your career, I would suggest to first understand the HVAC fundamentals, and learn manual calculations before dealing with softwares.
  2. ZDR1985

    Drain Pan for Thermal heat Wheel Section Required or Not?

    Possible condensation in plate heat exchanger?
  3. ZDR1985

    Humidifier Calculation

    What is your desired indoor condition? What is your sensible heat ratio? Are you using steam? Do you have a psychrometric chart? Do you have a steam table?
  4. ZDR1985

    Fire figthing at Biogas plant

    Check NFPA 850 (2015) Ch. 9.5
  5. ZDR1985

    Fire protection of an airport terminal building

    In my understanding the hose stream allowance is for combined inside and outside.
  6. ZDR1985

    Fire protection of an airport terminal building

    From NFPA 415 (2016) 4.5.5 Water Supply. Water supply from public or private sources shall be adequate to supply maximum calculated sprinkler demand plus a minimum of 500 gpm (1893 L/min) for hose streams. The supply shall be available at the rate specified for a period of at least 1 hour.
  7. ZDR1985

    Carrier's Hap - Airflow rates in summary report

    Did you mean a,b,c,d and e are not the same?
  8. ZDR1985

    Fire Hydrant Installation

    NFPA 24-2013 edition section 7.2.3 says not less than 12m from building or other structure, this is also used in one of our O&G project.
  9. ZDR1985

    Ventilation to prevent high temperature in chiller plant in basement

    EloyRD, 150 m2? That is a small room and ventilating it will result to over 40 air changes per hour, imagine that draft inside the room. Probably you have to double check on the chiller motors heat (open type or hermetic type), which maybe not that much as I assumed to be the same as pump...
  10. ZDR1985

    Ventilation to prevent high temperature in chiller plant in basement

    Hi, Why mechanical efficiency is used to estimate the heat generated by motors? Based on your data, assuming all pumps and chillers are running at the same time and motor heat dissipation is 5% of motor rating (95% efficiency), I get 72 kW of heat, that is approximately 6 m3/s (12,713 cfm) of...
  11. ZDR1985

    Chilled water pipe sizing.

    What is your delta T? For pipes 50mm and below, consider max velocity 1.2 m/s and max friction loss of 600 Pa/m. For pipes larger than 50mm, consider max velocity 2.4 m/s and max friction loss of 400 Pa/m. If it's in then you should be good.
  12. ZDR1985

    Basement Outdoor Air Ventilation

    That would be additional load to your split units, unless you cool it before you supply to basement.
  13. ZDR1985

    hydraulic calculation

    You need to read NFPA 13, everything is there.
  14. ZDR1985

    Electrical room exhaust fan

    RMERMP where you from? First, with just ventilation you cannot mainatain 24C inside if your outdoor temp is 28C, even 28C indoor will be unrealistic. Should be air conditioned to do that. Your delta T will be based on how much temp rise your electrical room will maintain at the peak of summer...