Recent content by wuqn

  1. wuqn

    Load shedding

    hi every body My underfrequency relay is used to remove load out of the generator (load shedding). I want to change the time delay. What delay is suitable ? How do i calculate the delay? the method ?
  2. wuqn

    TSX QUANTUM HARDWARE

    Dir sir/madam, My system's analog input card shows a fault led. After checked i found that the output voltage of an input was instable. Its flunctuates from 5-20 Vdc. The input is connected to a pressure transmitter. The system is TSX QUANTUM. The analog input card is 140 ACI 03000. What's the...
  3. wuqn

    power factor not stable

    i found the problem. droop variable resistor's wire is broken
  4. wuqn

    power factor not stable

    Thanks everybody. ScottyUK: the generatos are similar. rbulsara: the service is not good. Alex68: Can you show how to activate the AVR compound with a negative gain ? do I have to reduce the AVR's gain?
  5. wuqn

    power factor not stable

    the system has three paralelled generators. But the power factor of the two is not stable. one's PF increase then the other decrease. I don't know why. what's the problem? how can i fix it? thanks.
  6. wuqn

    start up current

    the system has one generator. How much is reserve power so that I can start up a large motor? Ex: generator: 480kW, motor: 110kW.
  7. wuqn

    compensate reactive power

    thank everybody. But what's happen when the generator has very low excitation and is absorbing leading VAr's? Can you explain more?
  8. wuqn

    compensate reactive power

    we have 3 generators that are paralleled. Can we use capacitors to compensate the reactive power of the system? we want to reduce the current through the generators.
  9. wuqn

    unbalance voltage

    the generator is 550kVA.
  10. wuqn

    unbalance voltage

    the stator is wye. the center point is grounded. it's ok when i put load on it. but the voltage is still unbalance. the generator is paralled with other generators. may be the ground resistance is high ?
  11. wuqn

    unbalance voltage

    3 phases. run unload
  12. wuqn

    unbalance voltage

    hi when generator run, measured voltages : Vab= 417, Vbc=420, Vca= 392. Vca is much lower than the others. what's the problem ? how can i fix it? thanks
  13. wuqn

    negative sequence current

    thank waross. the system has three paralleled generators. but one generator indicates :" negative sequence current is 2%". how can i do to fix it?
  14. wuqn

    checking equipment in zone 2

    inspecting and maintenance electrical apparatus
  15. wuqn

    negative sequence current

    droop, level and gain of AVR(automatic voltage regulator)'s is not set properly, can it cause negative sequence current ?