hi every body
My underfrequency relay is used to remove load out of the generator (load shedding). I want to change the time delay. What delay is suitable ? How do i calculate the delay? the method ?
Dir sir/madam,
My system's analog input card shows a fault led. After checked i found that the output voltage of an input was instable. Its flunctuates from 5-20 Vdc. The input is connected to a pressure transmitter. The system is TSX QUANTUM. The analog input card is 140 ACI 03000. What's the...
Thanks everybody.
ScottyUK: the generatos are similar.
rbulsara: the service is not good.
Alex68: Can you show how to activate the AVR compound with a negative gain ? do I have to reduce the AVR's gain?
the system has three paralelled generators. But the power factor of the two is not stable. one's PF increase then the other decrease. I don't know why. what's the problem?
how can i fix it? thanks.
we have 3 generators that are paralleled. Can we use capacitors to compensate the reactive power of the system? we want to reduce the current through the generators.
the stator is wye. the center point is grounded.
it's ok when i put load on it. but the voltage is still unbalance. the generator is paralled with other generators.
may be the ground resistance is high ?
hi
when generator run, measured voltages : Vab= 417, Vbc=420, Vca= 392.
Vca is much lower than the others. what's the problem ? how can i fix it? thanks