  1. wbd

    EasyPower License Transfer

    Hello, I have retired and am looking to transfer my EasyPower License. Any suggestions on where to post this? Other forums? Thanks in Advance
  2. wbd

    Generator Curves

    I have been asked to make some generator curves, a Decrement Curve and a Thermal Damage Curve using EasyPower software. The generator data sheets were provided and I have attached them here. I have found most of the information but am stuck on where to find: > Field Forcing current as a per...
  3. wbd

    Cable Limiter

    On an installation at a condominium complex the transformer is a 300kVA, 208/120V secondary. The secondary conductors are 500mcm AL 6 per phase. Transformer FLA is 832A so cable capacity is 1860A more than double transformer FLA. Each conductor has a BUSS Cable Limiter CDB-RV. I could not...
  4. wbd

    Blown "fuse" in transmission line (pictures)

    This cut-out is feeding a riser cable going to a pad mount transformer. Since the cut-out fuse blew and the cut out fuse holder fell open as it is designed to do, this would obviously indicate a fault. Therefore, I am surprised that the utility lineman just re-fused the cutout and closed it...
  5. wbd

    Lightning Arresters on a Delta System

    What benefit if any do LA'a provide on a 2400V delta distribution system? Thanks in advance.
  6. wbd

    Distribution Transformer Wildlife Protection

    I think I may have mis-stated my question. I was looking feedback on people's experience with particular guards. For example: tried xyz's guard on pole mounted transformers and they blew off on wind speeds greater than 40mph. Or ABC brand looked great but the linemen hated installing them...
  7. wbd

    Distribution Transformer Wildlife Protection

    Hello, I am working with a utility that is doing a 2400V delta to 4160V grounded wye conversion. One item that we are looking at is wildlife protection, mainly from birds. This is an island and there are no squirrels. It is an island so there is salt water so that may be consideration in...
  8. wbd

    Is it "legal" to stagger (3) single phase fuses of a 3-phase ckt in a control panel ?

    Is this existing industrial control panel UL listed? If so and UL listing is required, you may be invalidating that UL listing.
  9. wbd

    Arc Flash Mitigation on LV Switchboard

    Unless the barrier is a tested configuration, I don't believe you can take credit for it isolating an arcing fault. Unless it is specifically arc rated and testing equipment, I assume the arc will jump to the line side of the breaker and the upstream remote protective device will clear the...
  10. wbd

    Arc Flash, IEC 61641 "Arc Free" and NFPA 70E / IEEE 1584

    You may want to post this question in Jim Phillips' brainfiller arcflash forum as there are people there who have been on the standards committees and should be able to answer.
  11. wbd

    Old GE powermaster low voltage switchgear Arc flash incident

    Has to. They all came with a trip unit. It may be the original EC device.
  12. wbd

    Old GE powermaster low voltage switchgear Arc flash incident

    What was going on at the time? Was a breaker being racked in? Was it being closed? Was it being opened? Was there a fault on the circuit it feeds and it was tripping? What is the maintenance history of the breaker? What kind of trip units are on the breaker? Was it isolated to one breaker...
  13. wbd

    Determining the Short Circuit Current Rating (SCCR) of an unrated panel that has power and control

    The SCCR rating of the panel is 5kA as that is what is on the panel. That is what you have to live with. Just because people confuse terms such as available fault current, Have you modeled the system using the available fault current obtained from the utility? This would not be on a chart...
  14. wbd

    Battery maintenance schedule

    start with reviewing the manufacturer's manual and also the IEEE standards on batteries. I don't remember the std number as it has been a number of years since I dealt with batteries but there may be a inspection sheet in those that you can use. At the nuclear plants I worked at we used the DMA...
  15. wbd

    CB Short Circuit Rating

    What voltage are you at?