I just read IEC 63026 and can't find any reference to VLF withstand testing nor using VLF for TD and PD testing. Am I missing it or did they exclude it in the 2019 version?
Thanks Muthu for the info. I'll try to write up today an explanation of the motor test set's function with its multiple voltage taps for gradual motor starting. They are worried about the effects on their system and need assurances.
Thanks to all for your response.
This is a great forum for...
Thanks all. But one question still remaining is: if the motor under test is brought up to speed slowly, and never slammed on line, why do we care about starting currents, locked rotor currents, no load or full load currents in terms of the effect on the utility of the service is designed for...
The percent reduction will be the minimum needed to break over the torque to get it spinning, probably 60 - 65% of nominal.
The testing will be occasional as we rewind motors, but not everyday.
The soft start is the reduced voltage starting.
Thanks
Using a Motor Test Set with many reduced voltage taps. Utility worried about inrush on a 5000 HP, 12470V motor. Since we will be starting at lower voltages and working up, there will be no full v online starting currents. When will my max current occur? Need they worry?
Can anyone recommend a book or other materials to teach the design of oil insulated high voltage capacitors used in charge/discharge applications like thumpers/cable testers, energy pulse supplies, etc. Typical ratings are 10-20 kVdc @ 500J - 2000J.
Looking for company/consultant with design experience in high voltage AC supplies, particularly transformer design for low PD output. Also, bushing design for the same.
Any Siemens people out there to help? I am trying to find out the capacitance of a large HV motor so that we can size the power required from and AC hipot to perform overvoltage testing. I have the nameplate data.
Can anyone recommend one or more books for the design of high voltage, oil immersed transformers, particularly the design and processing steps necessary for low pd output.
Thank you.