I am not that much familiar with communication protocols. Can anyone suggest me some good reference so that I can study it from the Substation Communincation stand point.
Thanks in advance.
Do we traditionally install a Multifunction Protection Relay on a Low Voltage MCCB? Will it operate like a Power Circuit Breaker from a Protection Relay?
Thanks
I am working on a retrofit for 480 Cutler Hammer switchgear where the width of each section is 21". I have to install CTs and I need window type 3000/5A relaying CTs which can be placed side by side.Can anyone suggest me CTs with small dimensions and suitable window size (max. 3 inches) for such...
At how many times of rated current normally a metering CT saturates? I have a metering CT of 0.3B0.5, 600/5A class and want to use it with a protective relay which will pickup at 600A. Can I use this CT with the relay or I need a relaying class CT?
Thanks
Calculate the applicable derating factor as per NEC or IEC which ever is applicable and make sure that your cable can carry 168A after being derated.
For the derating due to grouping, refer to the vendor's catalogue. The optimum arrangement will depend upon the number of cables per group. It...
But I believe, by keeping one generator grounded at one time, you keep the other two in operation even if there is ground fault on the distribution side since all the generators are synchronised.