  1. sushilksk

    87T multi-terminal application

    CT location on 13.2kV side should be below tap point for correct operation of differential protection. Further, relay current at full load current on 13.2kV side will be 328A, which is too high to handle and not a good option of CT ratio.
  2. sushilksk

    "Zero offset" in tranformer's inrush current

    What you mean by "magnetic flux outside the iron core"? I have used term "DC offset" instead of "zero offset", both are same.
  3. sushilksk

    "Zero offset" in tranformer's inrush current

    It is due to saturation of magnetic core. In steady state, Flux produced in one half cycle is cancelled out by MMF of next half cycle. During charging, we need to close CB at exact point on wave (taking residual magnetism in account) to acheive normal current levels without any inrush...
  4. sushilksk

    Calculated neutral current not matching measured neutral current

    In this case THD is 2.7% and difference in neutral current is >50%. There should be some other issue.
  5. sushilksk

    Calculated neutral current not matching measured neutral current

    Neutral current should be = Vector sum of currents in all three phases. So, you need phasor angless.
  6. sushilksk

    GENERATOR DIFFERENTIAL CURRENT PROTECTION TRIP ISSUE

    From this, CT polarity is the probable cause of trip. Checking CT polarity and correcting is the solution. Further, regarding single point earthing for CT secondary circuit: Generally, one side set of three phase CTs make has siingle point earthing. And other side set of three phase CTs has...
  7. sushilksk

    Current transformers- over voltage on open circuiting secondary

    Practically, I have seen one CT failure due to CT open circuit in metering core at 132kV level. In all other cases, there was another current path developed by melting of cables / terminal blocks etc.
  8. sushilksk

    Current transformers- over voltage on open circuiting secondary

    violent failure of CT with explosion: It depends, if it is dead tank type CT with oil filled and porcelain housing, pressure developed can explode CT. In some cases over voltage can create insulation failure of cables, or terminal blocks, causing short circuit of CT secondary. In this case CT is...
  9. sushilksk

    DCDB EARTH FAULT

    DC earth fault locator kits (based on low frequency injection) are avaiable, which does not require isolation to some extent. But it needs expert person to identify exact location.
  10. sushilksk

    Bay control unit

    "bay controller unit" is an IED used for control and monitoring. It has all the functions of LCC and can be operated from Local or remote SCADA.
  11. sushilksk

    Three Position Switch in GIS

    Are you talking about three positions: [ol 1] Disconnector close, Earth switch open Disconnector open, Earth switch open Disconnector open, Earth switch close [/ol] It has advantage of having only one drive mechanism for both disconnector and earth switch.
  12. sushilksk

    Battery Cell Rating

    Temperature is missing in this rating. 105AH will at a particular temperature (Normally 27 deg C).
  13. sushilksk

    One phase current less during enrgization

    Does low inrush current is oberved always in C-phase, or it is changing randomly with every attempt? Is there any controlled switching device?
  14. sushilksk

    CT star formation

    CT star point is formed in the yard for EHV and UHV substaion.
  15. sushilksk

    Why do faults result in an arc on high-voltage systems?

    IMO, arc cuases melting of conductor. After melting, molten material will go down by gravity.