Everyone,
I need user manual or anything can help me to start working with SPI on INTools.
I've been on Intergraph website, there is nothing and found some links not available in their website anymore.
Any help would be highly appreciated.
Regards and thanks
The only thing is I am worried about is the bubbling surface of Deaerator may cause problem in Radar measurement.
Any experience with same type of service?
Thanks in advance.
Regards,
Ashereng,
I am not quite sure, since operations are insisting on replacement I did not ask more questions.
The only thing that I can think of is the tapping points of either high or low (or maybe both) might have blockage or something like that, although there are a lot of bends in tubing too...
Hi there,
We have a spray type deaerator in our boiler house.
The existing level measurement on this deaerator is Through a DP cell.
it has been found that slight pressure fluctuations in the top deaerator scrubber drum(i.e. a jump in steam pressure for only few psig), have had a huge impact on...
Thank you all for responses.
I have to clarify my question I believe:
I have a 2500 series Pneumatic level-trol controller from Fisher.
I want to convert this controller to just a Pneumatic transmitter with output signal usable for generating an alarm through a pressure switch and shutting...
Hi there,
I have a 2500 series level-trol pneumatic controller/transmitter from Fisher.
I want to convert this controller to just a pneumatic transmitter.
Can anybody help me? any link,reference,.. would be highly appreciated.
Regards
Hi there,
I have a 2500 series level-trol controller from Fisher.
I want to convert this controller to just a transmitter.
Can anybody help me? any link,reference,.. would be highly appreciated.
Regards
Everyone,
I have a magnetrol pneumatic level transmitter.
I do not have any model or other information for it.
I just know that is side and bottom connection.( I can not see it because of tracing around it but piping drawing shows that and we assume it is right)
It is installed on a 10"...
By splitter box I mean:
The outgoing cable after main breaker would go to a set of terminals which all of feeders to branch breakers are tied to those terminals.
As oppose to have a real bus bar and feed the branch circuit breaker from bus bar.
For 500kcmil I should use 7 conductor per phase...
Hi Everyone,
I have a 2000 kVA transformer 27.6 kV/ 600 V
The transformer and electrical service cabinet both are going to be outside and located very close by each other.
The code asks for breaker and conductor (secondary) not more than 125% of rated current.
1)What would be the most...
Everyone,
the motor is a Flygt mixer model 4670, here are some information they provide on their website:
Rated Power:14.9kW 20.0 hp
voltage:600 v
Speed (r/min):440
Rated Current: 36.0 A
No load Current: 28.0 A
Locked Rotor Current: 105.0 A
Starting kVA: 109.2
EEMAC CODE : F
Efficiency...
Hi there,
I have a large amout of mixers in my plant with low P.F.
(0.51 @ 100% load ).
There are 50 of them each 20 HP (600 V) and 36.0 A FLA. (High current)
With this P.F. I probably have to double size of transformer.
Or
Is there any way around this? what about capacitor banks?
I need...
Everyone,
I have an Existing Four way load break on my incoming 5 kV feeder and I am going to use one way to my new 500 kW transformer.
I need an illustrative reference indicating all HV components needed for Cable termination before XT primary.
Regards,
Everyone,
I have an existing MCC Panel.
One of the branches is 400A breaker feeding another MCC in other building Which its main incoming breaker is 500A.
Does anybody can see a reason behind that?
what If the total current of second MCC is more than 400?
Regards,