I post the paper here.
See page 273 equation(12)http://files.engineering.com/getfile.aspx?folder=6dd5b860-075f-4bfb-a2f7-924f25f36875&file=Effects_of_creep_and_shrinkage_on_the_deflection_of_RCC_two_way_flat_plates.pdf
asixth:
Could you provide any references for the caculations:
1. Short-term displacements...
delta_short=G+0.7*Q
2. Long-term displacments...
delta_long=(1+kcs)*G+(1+kcs)*0.4*Q
Especially, for "delta_long=(1+kcs)*G+(1+kcs)*0.4*Q"?
Thanks a lot.
I have come across a papers (“Effects of creep and shrinkage on the deflection of RCC two way flat plates”) which states that, in ACI 318-2000, the total deflection of two-way slab for the creep and shrinkage effect is calculated as three times the deflection due to dead and deflection due to...
structuresguy
Please see the attached file.
File's link is: http://files.engineering.com/getfile.aspx?folder=8ad87dfa-f5df-424a-819c-c555345ad514&file=Probleme_1_p.90.pdf
Shoulder edges(as you usually do)would lead to crack.
Please comment on this.
When the forms set tight to 3 sides,and a small gap on the fourth to pour in the grout, how to ensure that the air underneath the base plate can effectively get pushed out when grout gets in from the fourth side? I have read some grout installation instructions,which indicates that no air should...
structuresguy,
Thanks for your replies.
As you say,you have very rarely seen actually chamfered grout pads,and you pointed out in the next reply, "If it were not chamfered away from the plate, then the edges of the grout could easily crack due to be unconfined."
The question: Have you seen...
The column base plate grout usually needs to be chamfered 45-degree around the edges.
When does the guy on site do the chamfering? (The forms for the grouting have chamfer strips? or the edges of the grout chamfered after the forms removed?)
What kind of tool does the guy on site use in...
Girt Bracing
Question
08/01/2007
I am designing a building with vertical siding, channel girts, and sag rods. I was told that the industry standard is to consider the channel braced at the sag rods. How is this possible, since the sag rods are neither at the compression flange nor able to...
CSA S16-2001
19.1.5
For starred angle compression members interconnected at least at the one-third points, Clause 19.1.4 need not apply.
What does the one-third points refer to here?
Thanks in advance.
Load and Resistance Factor
Design Specification for
Steel Hollow
Structural Sections November 10, 2000
4.1.1(c)In frames for which lateral stability is provided by diagonal bracing, shear walls or equivalent means, K shall be taken as unity, unless a lesser value can be justified by rational...