  1. stason

    Overvoltage relay low pass filter cutoff frequency

    I am not sure we are talking about the same filter. I was talking about an analog low pass filter sitting behind the voltage transformers. I am simulating its behavior before the A/D converter. And from what I know the cutoff frequency = 1/(2*pi*R*C)
  2. stason

    Overvoltage relay low pass filter cutoff frequency

    with the sampling rate of 1.25 ms that would lead to something like 63 Hz cutoff, which would cause a pretty strong reduction of the 50Hz when using the first-order low pass. But, the relay manual does not reveal the type of filter used. Thanks, pete, that's already something to start with.
  3. stason

    Overvoltage relay low pass filter cutoff frequency

    Hello all, can anybody tell me what the cutoff frequency of the input low pass filter of a voltage / frequency protection relay, such as e.g. SEG MRN3, would be? The manual says the relay applies an analog filter to get rid of higher harmonics before it applies digital DFT filtering. I am...
  4. stason

    Overcurrent relay at generators: True RMS / DC ?

    dpc, According to wikipedia: # 50 - Instantaneous Overcurrent Relay # 51 - AC Inverse Time Overcurrent Relay so I asked if the definite time OC relay would also trip due to overcurrent at one phase only. BTW, does the Def.time OC relay have an ANSI number as well or does it share 51 with the...
  5. stason

    Overcurrent relay at generators: True RMS / DC ?

    Thank you! a 51 is an inverse time OC element. What about the definite time OC element and instantaneous one?
  6. stason

    Overcurrent relay at generators: True RMS / DC ?

    Hi guys, I am still new to protection system, so don't judge too hard. A 3-phase overcurrent relay at a generator normally monitors each phase and will pick up and subsequently trip the generator even if the current at ONE phase only exceeds the threshold, right? For example due to too high...
  7. stason

    Flux of a transformer decays to zero when left connected to load

    Thanks Bronzeado, going back to the 90s sounds good. ;) But I am graduating in 2 weeks, so I will get back at you in a couple of weeks. Best regards
  8. stason

    Flux of a transformer decays to zero when left connected to load

    Or maybe these two effects will exactly compensate each other so that the decay has the same rate?!
  9. stason

    Flux of a transformer decays to zero when left connected to load

    Hi Bronzeado, I have another thought about the sympathetic inrush. Maybe you could contribute to it?! If I have several (let's say 3) transformers in parallel and one of them is being energized driving the other two into sympathetic interaction, will the sympathetic inrush last longer because...
  10. stason

    Overcurrent relay at generators: True RMS / DC ?

    Thank you! Another question: are instantaneous pickup currents defined in Apeak or Arms? If an instantaneous current relay should operate with a 0,04 sec time delay, I suppose the corresponding curent pickup value is defined in Arms, since the relay has 2 whole periods (50 Hz) to measure the...
  11. stason

    Overcurrent relay at generators: True RMS / DC ?

    Hi guys, what current is usually measured by the overcurrent protective relays installed at synchronous generators below 10 MVA? Do they measure the true rms value (that is, all harmonics) or are some harmonics filtered out? How about the DC offset during a fault or transformer inrush? Is...
  12. stason

    Flux of a transformer decays to zero when left connected to load

    Hi folks, a kind of a different question: what is the flow path of the decaying DC offset component in the transformer current? It also appears at the generator. Does it only flow in the generator stator or also the rotor? And what is the return path to the transformer if the generator neutral...
  13. stason

    Flux of a transformer decays to zero when left connected to load

    Hi Bronzeado, thanks. I found a paper by you and Yacamini dating back to 1996 with the thorough explanation. I find it pretty good! Regards
  14. stason

    Flux of a transformer decays to zero when left connected to load

    Let me express it better: The inrush current of the transformer being energized is predominantly homopolar so that the voltage drop affects only one half-cycle. Let's say the fist half-cycle is positive, then the voltage drop makes this positive value to decrease. The waveform of the opposite...
  15. stason

    Flux of a transformer decays to zero when left connected to load

    A somewhat different question regarding sympathetic inrush of transformers connected in parallel or in series. Literature says the offset current of the already running transformer is of opposite polarity to that of the one being energized. Is that because the voltage drop across the system...